Introduction

This article describes a DLL assembly (myOPC.DLL) that wraps Interop.OPCAutomation.DLL which Interops the COM OPCDAAuto.DLL. Both of these were created by OPC Foundation and uses DA1 (Data Access 1) which was the original OPC (OLE for Process Control) standard. myOPC.DLL makes it easier to create a client that communicates to a device through an OPC server. This article will first describe the myOPC.DLL wrapper and then give real world examples of how to use it in a client .NET program.

Background

I was tasked to create a PC program that could interface with a PLC (Programmable Logic Controller). At the time I was using VB.NET for my PC application development. Searching for a .NET solution I soon discovered that OPC was the optimum choice. I'm not going into the basics of OPC as this has been done by several people with my favorite here. To communicate with a device (e.g. PLC) through a channel (e.g. Ethernet, Serial) to a PC program an OPC server is used. Most modern OPC servers allow for the use of three main OPC standards. These are Data Access (DA) version 1-3, Unified Architecture (UA), and OPC .NET 3.0. The last one seems to be a standard the OPC Foundation would prefer never existed. The UA standard is the latest standard and is independent of COM and thus Microsoft. However, when looking for example client code that communicated with OPC servers I could only find a DA1 example. My organization does not have the cash it takes to be an OPC Foundation member where one can find SDK's and examples for the UA standard. I found VB.NET client examples on the OPC server company Kepware web site. With this example and my knowledge of object oriented programming I created a wrapper that extracted out the ugly details of using the Interop.OPCAutomation.DLL.

Describing The DLL Code Starting With The StartOPC Function

The first procedure examined is the function StartOPC(). After creating an instance of the myOPC.DLL in the client and setting some properties this function starts the OPC connection. The returned Boolean indicates success (True) or failure (False) at starting this connection. The below is the complete code for this function that I present for clarity. This will be followed with detail explanations of sections of this function to describe the more important concepts in this function. Please note that the function starts out by checking that pivotal properties and fields have been set by the object user. The connection will not attempt to start if any of these are empty and will return a false.

VB
''' <summary>
''' Creates the OPC connection, Groups, Items then activates and reads item values 
''' as long as no errors occur along the way.
''' </summary>
Public Function StartOPC() As Boolean
    Try
        ' First verify that all of the parameters have been set up
        ' before starting OPC connection.
        If Not _DeadBand = Nothing _
        Or Not _UpdateRate = Nothing _
        Or Not _GroupName = Nothing _
        Or Not _NumItems = Nothing _
        Or ((Not _TopicName = Nothing) Or (Not _CameraName = Nothing) Or _
                  ((Not _ChannelName = Nothing) And (Not _DeviceName = Nothing))) Then
            For j As Integer = 1 To _NumItems
                If OPCItemNames(j) Is Nothing Then
                    If _SilentMode = False Then
                        MessageBox.Show("Set the OPC parameters before opening connection", "Error", MessageBoxButtons.OK)
                    End If
                    Return False
                End If
            Next
            ' Create a new OPC Server object
            _ConnectedOPCServer = New OPCServer
            ' Attempt to connect with the server
            _ConnectedOPCServer.Connect(_OPCserver, "")
            ' Set the desire active state for the group
            _ConnectedOPCServer.OPCGroups.DefaultGroupIsActive = True
            ' Set the desired percent dead band
            _ConnectedOPCServer.OPCGroups.DefaultGroupDeadband = _DeadBand
            ' Add the group
            _ConnectedGroup = _ConnectedOPCServer.OPCGroups.Add(_GroupName)
            ' Set the update rate for the group
            _ConnectedGroup.UpdateRate = _UpdateRate
            ' Mark this group to receive asynchronous updates via the DataChange event.
            _ConnectedGroup.IsSubscribed = _AsynchMode
            ' Setting the '.DefaultIsActive' property forces all items we are about to
            ' add to the group to be added in a non active state.
            _ConnectedGroup.OPCItems.DefaultIsActive = False
            ' Assemble the OPC Item IDs
            For i As Integer = 1 To _NumItems
                ' Define item name based on which OPC server utilized.
                Select Case _OPCServerType
                    Case 1 'RSLinx OPC Server
                        _OPCItemIDs(i) = String.Format("[{0}]{1}", _TopicName, CStr(OPCItemNames(i)))
                    Case 2 'Kepware OPC Server
                        _OPCItemIDs(i) = String.Format("{0}.{1}.{2}", _ChannelName, _DeviceName, CStr(OPCItemNames(i)))
                    Case 3 'Cognex OPC Server
                        _OPCItemIDs(i) = String.Format("{0}.{1}", _CameraName, CStr(OPCItemNames(i)))
                End Select
                ' Define the Client Handle
                _ClientHandles(i) = i
            Next
            ' Add the items
            _ConnectedGroup.OPCItems.AddItems(_ItemCount, _OPCItemIDs, _
                       _ClientHandles, _ItemServerHandles, _AddItemServerErrors)
            ' For the items added without errors make them active 
            For i = 1 To _NumItems
                If _AddItemServerErrors(i) <> 0 Then
                    ' Set the active type desired.
                    _ActiveState = False
                    ' Get the Servers handle for the desired item. The server handles
                    ' were returned in add item subroutine.
                    _ActiveItemServerHandles(1) = _ItemServerHandles(i)
                    ' Invoke the SetActive operation on the OPC item collection interface
                    _ConnectedGroup.OPCItems.SetActive(1, _ActiveItemServerHandles, _ActiveState, _ActiveItemErrors)
                    ' Inform user of class is not active because of faults.
                    OPCItemActive(i) = False
                Else
                    ' Set the active type desired.
                    _ActiveState = True
                    ' Get the Servers handle for the desired item. The server handles
                    ' were returned in add item subroutine.
                    _ActiveItemServerHandles(1) = _ItemServerHandles(i)
                    ' Invoke the SetActive operation on the OPC item collection interface
                    _ConnectedGroup.OPCItems.SetActive(1, _ActiveItemServerHandles, _ActiveState, _ActiveItemErrors)
                    ' If an error occurred during activation then deactivate the user info.
                    OPCItemActive(i) = True
                End If
                ' Get the Servers handle for the desired item. The server handles were
                ' returned in add item subroutine.
                _SyncItemServerHandles(i) = _ItemServerHandles(i)
                _RemoveItemServerHandles(i) = _ItemServerHandles(i)
            Next
            ' Invoke the SyncRead operation. Remember this call will wait until
            ' completion. The source flag in this case, 'OPCDevice' , is set to
            ' read from device which may take some time.
            _ConnectedGroup.SyncRead(OPCDataSource.OPCDevice, _ItemCount, _
                     _SyncItemServerHandles, _SyncItemValues, _SyncItemServerErrors)
            ' Collect data read and if any errors occurred or the item is not
            ' active then zero out the value sent to the user.
            For i = 1 To NumItems
                If OPCItemActive(i) Then
                    If _SyncItemServerErrors(i) = 0 Then
                        OPCItemValues(i) = _SyncItemValues(i)
                    Else
                        OPCItemValues(i) = 0
                        Return False
                    End If
                Else
                    OPCItemValues(i) = 0
                End If
            Next
            Return True
        Else
            If _SilentMode = False Then
                MessageBox.Show("Set the OPC parameters before opening connection", _
                                 "Error", MessageBoxButtons.OK)
            End If
            Return False
        End If
    Catch ex As Exception
        ' Error handling
            _ConnectedOPCServer = Nothing
        If _SilentMode = False Then
            MessageBox.Show("OPC server connect failed with exception: " + _
                       ex.Message, "myOPC Exception", MessageBoxButtons.OK)
        End If
        Return False
    End Try
End Function

Creating The OPC Server Object

The first thing required to start the OPC is to instantiate a new OPC server object. Once this object is created a connection is made to the actual OPC server. The first parameter, _OPCserver, is a string of the name of the OPC server being used called ProgID. These values were discovered using the discovery example found on the Kepwareweb site. The second parameter is called Node and is an object. It is not clear to me what this is used for and because the connection worked without it I just used what the Kepware example used (i.e. ""). The way that user of this DLL specifies the OPC server ProgID is through the OPCServerType integer property which must be set before starting the OPC server. The property in turns sets the _OPCserver to the proper string. If you use a different OPC server company than I do you will have to modify the DLL for a 4th OPC type that sets the appropriate string for your OPC server.

OPCServerType Value   =>     _OPCserver Value
1      =>     "RSLinx OPC Server"
2      =>     "Kepware.KEPServerEX.V5"
3      =>     "Cognex In-Sight OPC Server"
VB
' Create a new OPC Server object
_ConnectedOPCServer = New OPCServer
' Attempt to connect with the server
_ConnectedOPCServer.Connect(_OPCserver, "")

Creating The OPC Group

The OPC group is next to be created and defined. The group houses the OPC items and define some of their behavior. The first step is to make groups default to be active. Next the dead band is set via the property DeadBand. The dead band is an integer that is kept to a value of 0 to 99 via the DeadBand property. The dead band is only valid for an asynch group. If set to zero then any change in the group items will cause an asynch read of the changed item. If the value is 10, for example, then the asynch read will occur when the item value changes +/- 10%. Next the group is created with the string name of the group set with _GroupName. I found that this string is useful in troubleshooting. The update rate is next to be defined with the property UpdateRate. This property is an integer and represents the update rate of the group in milliseconds. When I have multiple connections to the same device I set each update rates at a different prime number. Also keep in mind it is possible for some OPC servers to optionally over ride this rate. The UpdateRate is followed with setting the Boolean property called AsynchMode. When AsynchMode is set to False the values of the items in the group can only be discovered through a manual client OPC read. Inversely when set to True a method will be raised every time the value changes based on DeadBand and UpdateRate. Synchronous and Asynchronous modes will be described more later in this article. The last group thing modified is the DefaultIsActive set to False forcing the items to be added in a non active state. Items should not be made active until they are confirmed working with no faults.

VB
' Set the desire active state for the group
_ConnectedOPCServer.OPCGroups.DefaultGroupIsActive = True
' Set the desired percent dead band
_ConnectedOPCServer.OPCGroups.DefaultGroupDeadband = _DeadBand
' Add the group
_ConnectedGroup = _ConnectedOPCServer.OPCGroups.Add(_GroupName)
' Set the update rate for the group
_ConnectedGroup.UpdateRate = _UpdateRate
' Mark this group to receive asynchronous updates via the DataChange event.
_ConnectedGroup.IsSubscribd = _AsynchMode
' Setting the '.DefaultIsActive' property forces all items we are about to
' add to the group to be added in a non active state.
_ConnectedGroup.OPCItems.DefaultIsActive = False

Creating The OPC Items

After the OPC group has been created and defined the OPC items can be added. This process uses the NumItems property to set up the For loop.  NumItems also re-DIMs the Item arrays. Make sure the number of itemID's added matches the NumItems. The two tricky items for me creating this DLL was determining the progID and the ItemID. From the below code it can be seen that the string for ItemID is formatted significantly differently for each OPC server type. The only common portion of this format is the OPCItemNames array defined by the client. This array gives the address in the device of the items being tracked, I call them tags. The format of these tags can also be confusing. Fortunately Kepware has done a great job of documenting them. My example will use Allen Bradley PLC tags. Notice that certain properties pertain to the OPC server type chosen. For example if you are using a RSLinx OPC server only the TopicName is required and the ChannelName, DeviceName, and CameraName can be left undefined. Note two things from the below For loop, the first being that the arrays used in an OPC server is One based not Zero. Second notice inside the For loop the _ClientHandles is defined with the For loop index. Once the ItemID array has been defined then all of the items set up by the client is added at once. This method calls to the connected group to add items and has five parameters. The _ItemCount is equal to _NumItems. I know what your thinking and no I don't know why I didn't just use _NumItems. The array _OPCItemIDs is what we just created which contains the OPC items ID (i.e. the complete address). The _ClientHandles, also just created, represents a number used by the client for reading and writing the specific item desired. The forth and fifth parameters are set by the OPC server call not the client. The _ItemServerHandles is similar to the _ClientHandles except that it is created by the server.

_ItemServerHandles
will be used for synchronous reads. The last parameter is used to inform of any errors that occurred.

VB
' Assemble the OPC Item IDs
For i As Integer = 1 To _NumItems
    ' Define item name based on which OPC server utilized.
    Select Case _OPCServerType
        Case 1 'RSLinx OPC Server
            _OPCItemIDs(i) = String.Format("[{0}]{1}", _TopicName, CStr(OPCItemNames(i)))
        Case 2 'Kepware OPC Server
            _OPCItemIDs(i) = String.Format("{0}.{1}.{2}", _ChannelName, _DeviceName, CStr(OPCItemNames(i)))
        Case 3 'Cognex OPC Server
            _OPCItemIDs(i) = String.Format("{0}.{1}", _CameraName, CStr(OPCItemNames(i)))
    End Select
    ' Define the Client Handle
    _ClientHandles(i) = i
Next
' Add the items
_ConnectedGroup.OPCItems.AddItems(_ItemCount, _OPCItemIDs, _
        _ClientHandles, _ItemServerHandles, _AddItemServerErrors)

Activate The OPC Items

Now that the items have been added to the group the items without errors are made active. I know this bit of code could use some refactoring. After making the items active all of the items in the group are read. I have since wondered if I should have added this functionality. The problem arrives in asynchronous mode in that the asynch method is called when the StartOPC() function is ran. Depending on your application this can be a problem. The final thing I want to mention here is about the SilentMode Boolean property. Looking at the full code above it can be seen that all of this logic is wrapped in a try..catch block. This message box is used to inform the client that an error occurred when the SilentMode is set to False. Once I go from development to production I set SilentMode property to True as I have worked out any bugs.

VB
' For the items added without errors make them active 
For i = 1 To _NumItems
    If _AddItemServerErrors(i) <> 0 Then
        ' Set the active type desired.
        _ActiveState = False
        ' Get the Servers handle for the desired item. The server handles
        ' were returned in add item subroutine.
        _ActiveItemServerHandles(1) = _ItemServerHandles(i)
        ' Invoke the SetActive operation on the OPC item collection interface
        _ConnectedGroup.OPCItems.SetActive(1, _ActiveItemServerHandles, _ActiveState, _ActiveItemErrors)
        ' Inform user of class is not active because of faults.
        OPCItemActive(i) = False
    Else
        ' Set the active type desired.
        _ActiveState = True
        ' Get the Servers handle for the desired item. The server handles
        ' were returned in add item subroutine.
        _ActiveItemServerHandles(1) = _ItemServerHandles(i)
        ' Invoke the SetActive operation on the OPC item collection interface
        _ConnectedGroup.OPCItems.SetActive(1, _ActiveItemServerHandles, _ActiveState, _ActiveItemErrors)
        ' If an error occurred during activation then deactivate the user info.
        OPCItemActive(i) = True
    End If
    ' Get the Servers handle for the desired item. The server handles were
    ' returned in add item subroutine.
    _SyncItemServerHandles(i) = _ItemServerHandles(i)
    _RemoveItemServerHandles(i) = _ItemServerHandles(i)
Next

Describing other important methods in the DLL assembly

The Asynchronous Functionality

If the client sets the OPC group to be asynchronous the below method will fire every time one or more items changes within the dead band. This method receives the number of items effected and their corresponding client handles from the OPC server. Through the use of this information this method will update the item fields that changed related to the OPC item value, quality, and time stamp. Once the changed items have been updated the method OPCdataChanged() is called. This method is meant for the client to over-ride it so it can be informed of a change of data. I will show this in the example but this DLL can be used in two main ways. If used in synchronous mode then myOPC.DLL is instantiated directly. Otherwise a class should be created that inherits from myOPC.DLL. In this way this new class can over-ride the OPCdataChanged() method and use it as required.

VB
Private Sub _ConnectedGroup_DataChange(ByVal TransactionID As Integer, _
        ByVal NumItems As Integer, ByRef ClientHandles As System.Array, _
        ByRef ItemValues As System.Array, ByRef Qualities As System.Array, _
        ByRef TimeStamps As System.Array) Handles _ConnectedGroup.DataChange
    Try
        Dim i As Integer
        For i = 1 To NumItems
            ' Use the 'ClientHandles' array returned by the server to pull out the
            ' index number of the control to update and load the value.
            OPCItemValues(ClientHandles(i)) = ItemValues(i)
            OPCItemQuality(ClientHandles(i)) = OPCquality(Qualities(i))
            OPCItemTimeStamp(ClientHandles(i)) = TimeStamps(i)
        Next i
            OPCdataChanged()
    Catch ex As Exception
            ' Error handling
            If _SilentMode = False Then
                MessageBox.Show("OPC DataChange failed with exception: " + _
                          ex.Message,"myOPC Exception",MessageBoxButtons.OK)
            End If
    End Try
End Sub

Protected Overridable Sub OPCdataChanged()
    ' Add your crap here
End Sub

Synchronous Item Read

If the client sets the OPC group to be Synchronous the below Boolean function can be used to manually read individual items. If all goes well a True will be returned and the corresponding field value will be updated (i.e., OPCItemValues(ItemClientHandle)). OPCItemValues() is an array of objects that contains the OPC item value regardless of the mode (e.g., synchronous or asynchronous). The ItemClientHandle is the parameter required for the OPCsynchRead() function that points to the desired item to be updated. Notice that because OPCItemValues() are objects a cast will be required before the client can effectively use them. The first thing this function does is verify that the value of ItemClientHandle is legitimate. After looking up the server item handle this code performs a SynchRead on the specified item. If the synchronous read returns no errors then the specified OPC item value, quality, and time stamp will be updated. Note that a nearly identical function also exists that uses the item name as the parameter instead of the item handle.

VB
''' <summary>;
''' Synchronously read data from the PLC tag pointed to by the parameters.
''' Returns True if the read process worked.
''' </summary>
Public Function OPCsynchRead(ByVal ItemClientHandle As Integer) As Boolean
    Try
        If ItemClientHandle > _NumItems Or ItemClientHandle < 1  Then
            ' Error handling
            If _SilentMode = False Then
                MessageBox.Show("OPC Item Handle Does Not Exist: ", _
                          "myOPC Item Missing", MessageBoxButtons.OK)
            End If
            Return False
        End If
        ' Add the found item handle in the Sync one.
        _SyncItemServerHandles(1) = _ItemServerHandles(ItemClientHandle)
        ' Read the new item value into the requested 
        _ConnectedGroup.SyncRead(OPCDataSource.OPCDevice, 1, _SyncItemServerHandles, _
                _SyncItemValues, _SyncItemServerErrors, _SyncItemQuality, _SyncItemTimeStamp)
        If _SyncItemServerErrors(1) = 0 Then
            OPCItemValues(ItemClientHandle) = _SyncItemValues(1)
            OPCItemQuality(ItemClientHandle) = OPCquality(_SyncItemQuality(1))
            OPCItemTimeStamp(ItemClientHandle) = _SyncItemTimeStamp(1)
            Return True
        Else
            OPCItemValues(ItemClientHandle) = Nothing
            OPCItemQuality(ItemClientHandle) = "Bad"
            ' Error handling
            If _SilentMode = False Then
                MessageBox.Show("OPC read failed: " & _SyncItemServerErrors(1), _
                             "myOPC Read Failed", MessageBoxButtons.OK)
            End If
            Return False
        End If
    Catch ex As Exception
        ' Error handling
        If _SilentMode = False Then
            MessageBox.Show("OPC read failed: " & ex.Message, _
                        "myOPC Read Failed", MessageBoxButtons.OK)
        End If
        Return False
    End Try
End Function

Synchronous Group Read

Alternatively we can read all items within the group at once with the below Boolean function. It requires no parameters and returns a True if all goes well. The logic is nearly the same to the above except that it loops through all the item handles and reads them.

VB
''' <summary>
''' Synchronously reads all the data in the group from the PLC tag pointed to by the parameters.
''' Returns True if the read process worked.
''' </summary>
Public Function OPCsynchReadGroup() As Boolean
    Dim ServerErrorOccured As Boolean = False
    Try
        For j As Integer = 1 To _NumItems
        ' Add the found item handle in the Sync one.
            _SyncItemServerHandles(j) = _ItemServerHandles(j)
        Next
        ' Read the new item value into the requested item.
        _ConnectedGroup.SyncRead(OPCDataSource.OPCDevice, _NumItems, _SyncItemServerHandles, _
                  _SyncItemValues, _SyncItemServerErrors, _SyncItemQuality, _SyncItemTimeStamp)
        For k As Integer = 1 To _NumItems
            If _SyncItemServerErrors(k) = 0 Then
                OPCItemQuality(k) = OPCquality(_SyncItemQuality(k))
                OPCItemValues(k) = _SyncItemValues(k)
                OPCItemTimeStamp(k) = _SyncItemTimeStamp(k)
            Else
                ServerErrorOccured = True
                OPCItemValues(k) = Nothing
                OPCItemQuality(k) = "Bad"
            End If
        Next
        If ServerErrorOccured = True Then
            ServerErrorOccured = False
            If _SilentMode = False Then
                MessageBox.Show("OPC read failed: " & _SyncItemServerErrors(1), _
                            "myOPC Read Failed", MessageBoxButtons.OK)
            End If
            Return False
        Else
            Return True
        End If
    Catch ex As Exception
        ' Error handling
        If _SilentMode = False Then
            MessageBox.Show("OPC read failed: " & ex.Message, _
                          "myOPC Read Failed", MessageBoxButtons.OK)
        End If
        Return False
    End Try
End Function

Synchronous Item Write

If an item needs to be changed by your client program than OPCwrite() is the Boolean function for you. Again if all goes well this function will return a True. The function accepts two parameters the first representing the new value and the second the handle of the item. Once the handle is verified the function writes the items new value. If any errors occur along the line a False is returned. Note that a nearly identical function also exists that uses the item name as the parameter instead of the item handle.

VB
''' <summary>
''' Writes Data to the PLC tag pointed to by the parameters.
''' Returns TRUE if the write process worked.
''' </summary>
Public Function OPCwrite(ByVal NewItemValue As Object,ByVal ItemClientHandle As Integer) As Boolean
    Try
        ' Check to make sure the imported handle is within the boundaries
        ' between 1 and the number of items.
        If ItemClientHandle > _NumItems Or ItemClientHandle < 1 Then
            ' Error handling
            If _SilentMode =False Then
                MessageBox.Show("OPC Item Handle Does Not Exist: ", _
                          "myOPC Item Missing", MessageBoxButtons.OK)
            End If
            Return False
        End If
        ' Add the imported NewItemValue into the Sync one.
        _SyncItemValues(1) = NewItemValue
        ' Add the imported item handle into the Sync
        _SyncItemServerHandles(1) = _ItemServerHandles(ItemClientHandle)
        ' Write the new item value into the requested
        _ConnectedGroup.SyncWrite(1, _SyncItemServerHandles, _SyncItemValues, _SyncItemServerErrors)
        If _SyncItemServerErrors(1) <> 0Then
            Return False
        Else
            Return True
        End If
    Catch ex As Exception
        ' Error handling
        If _SilentMode = False Then
            MessageBox.Show("OPC Write failed with exception: " + _
                      ex.Message, "myOPC Exception", MessageBoxButtons.OK)
        End If
        Return False
    End Try
End Function

Close Connection

Be a good steward and close the OPC connection with the below method. If you fail to close the connection while closing the program and/or form the group and its items will remain active at the OPC server. This method closes in the same way it opens but in reverse order.

VB
''' <summary>
''' Allows for the OPC connection to be safely disconnected.
''' </summary>
Public Sub Close()
    Try
        ' Remove the items from the group
        _ConnectedGroup.OPCItems.Remove(_ItemCount, _RemoveItemServerHandles, _RemoveItemServerErrors)
        ' Remove the group from the server before closing the form
        _ConnectedOPCServer.OPCGroups.Remove(_GroupName)
        ' Disconnect from OPC server before closing the form
        _ConnectedOPCServer.Disconnect()
    Catch ex As Exception
        ' Error handling
        If _SilentMode = False Then
            MessageBox.Show("OPC Dispose failed with exception: " + _
                          ex.Message,"myOPC Exception",MessageBoxButtons.OK)
        End If
    End Try
End Sub

Download Files

Two main zip files are provided. The first is visual studio 2010 solution that compiles the myOPC.dll assembly. If you wish to improve or add to this object then you will need this zip file. If your just going to use the DLL file for your client needs then the second zip file is all that is required. Inside this zip file you will find several files. The files myOPC.dll and Interop.OPCAutomation.dll both should be referenced by your client file and their properties "Copy Local" set to true. The file Interop.OPCAutomation.dll will have to have its property "Embed Interop Types" set to False first. On every machine your client program uses myOPC.dll the assembly OPCDAAuto.dll must also be located and registered to the that machines operating system. This registration is done via the included update_OPCdaauto.bat file. If you don't do this (and you will forget) the assembly myOPC.dll will not function. I usually copy both OPCDAAuto.dll and the batch file to the System32 directory of the machine I'm going to use than run the batch file.

Client Example

The below example is a simple windows form that creates a synchronous and asynchronous OPC connection when the form loads. Don't forget to reference myOPC.dll and Interop.OPCAutomation.dll and register OPCDAAuto.dll just explained. The below is a common scenario for my use of an OPC connection to a PLC (Allen Bradley in this case). The example also uses a Kepware server already set up with ChannelName and DeviceName. When something in a manufacturing process occurs like the end of a machine cycle a bit usually gets set indicating such. This bit is being watched by an asynchronous group and runs the inherited/overloaded method OPCdataChanged(). Then code is added to OPCdataChanged to grab and record process data and reset the trigger flag. The last thing I want you to remember is the need to convert OPC items before using them as they come back as objects.

VB
Public Class Form1
    ' Create OPC instances
    Public myAsynchOpc As AsynchOpc = New AsynchOpc
    Public mySynchOpc As myOPC.myOPC = New myOPC.myOPC

    Private Sub Form1_Load(sender As Object, e As EventArgs) HandlesMyBase.Load
        ' Define Asynchronous Parameters
        myAsynchOpc.AsynchMode = True
        myAsynchOpc.ChannelName = "my2Channel"
        myAsynchOpc.DeviceName = "my2Device"
        myAsynchOpc.DeadBand = 0
        myAsynchOpc.GroupName = "myAsynchGroup"
        myAsynchOpc.NumItems = 1
        myAsynchOpc.OPCServerType = 2
        myAsynchOpc.SilentMode = False
        myAsynchOpc.UpdateRate = 100
        myAsynchOpc.OPCItemNames(1) = "myTrigger"

        ' Define Synchronous Parameters
        mySynchOpc.AsynchMode = False
        mySynchOpc.ChannelName = "my2Channel"
        mySynchOpc.DeviceName = "my2Device"
        mySynchOpc.DeadBand = 0
        mySynchOpc.GroupName = "mySynchGroup"
        mySynchOpc.NumItems = 2
        mySynchOpc.OPCServerType = 2
        mySynchOpc.SilentMode = False
        mySynchOpc.UpdateRate = 100
        mySynchOpc.OPCItemNames(1) = "myData[0]"
        mySynchOpc.OPCItemNames(2) = "myData[1]"

        Try 'Start OPC's
            Dim asynchOpcStarted As Boolean = myAsynchOpc.StartOPC()
            Dim synchOpcStarted As Boolean = mySynchOpc.StartOPC()
            ' Add logic to verify they started
        Catch ex As Exception
            ' Error Logic Here
        End Try
    End Sub

    ' Don't forget to be a good steward and close OPC connections
    Private Sub Form1_FormClosing(sender As Object, _
                e As FormClosingEventArgs)Handles MyBase.FormClosing
        myAsynchOpc.Close()
        mySynchOpc.Close()
    End Sub

    Public Class AsynchOpc
            Inherits myOPC.myOPC

        Protected Overrides Sub OPCdataChanged()
            MyBase.OPCdataChanged()

            ' Shown for clarity could inline this
            Dim theTrigger As Boolean = Convert.ToBoolean(OPCItemValues(1))

            If theTrigger = True Then
                ' If the trigger is on read data
                Form1.mySynchOpc.OPCsynchReadGroup()
                ' Grab Data
                Dim Data0 As Int32 = Convert.ToInt32(Form1.mySynchOpc.OPCItemValues(1))
                Dim Data1 As Int32 = Convert.ToInt32(Form1.mySynchOpc.OPCItemValues(2))
                ' Reset Trigger
                OPCwrite(0,1)
            End If
        End Sub
    End Class
End Class

Final Thoughts

This assembly was my first OO attempt. I had moved from VB6 to VB.NET with little knowledge of the OO world and its best practices. I made some major mistakes like using a message box instead of raising an exception. I also made minor mistakes like incorrect casing and things in between. So why didn't I change it?  I did not have time and the assembly worked well for what I was doing at the time. I am currently creating a new version of this assembly with C# and Advosol wrapper instead of OPC foundation. This will give me DA3 instead of DA1 and with my improved .NET knowledge should result in a more efficient and powerful way of communicating with OPC devices.

History

  • 5/2008 - myOPC.dll created.
  • 6/2010 - myOPC.dll final revision.
  • 11/2012 - Article submitted.

License

This article, along with any associated source code and files, is licensed under The Code Project Open License (CPOL)


Written By
Software Developer (Senior) Action Equipment Solutions
United States United States
My first love was computers born from my Commodore 64 in the early 80's. Because the market was flooded with CS majors I choose control engineering instead. Control engineering is a nice blend of programming and hardware. It has been a sheer joy working with new systems, vision, robotics, PLC platforms, electrical design, etc. Recently my focus has been software development and I am having a blast programming C# .NET applications down here in the bluegrass.

Comments and Discussions

 
QuestionCLP Allen Bradley Pin
Member 1520677819-May-21 13:53
Member 1520677819-May-21 13:53 
QuestionUnable to cast object of type 'System.Int32[*]' to type 'System.Int32[]'. Pin
Member 147119229-Jan-20 11:13
Member 147119229-Jan-20 11:13 
AnswerRe: Unable to cast object of type 'System.Int32[*]' to type 'System.Int32[]'. Pin
Kurt Swaim21-Jun-20 13:23
Kurt Swaim21-Jun-20 13:23 
QuestionDear Sir, myOPC.dll Open Source Pin
FIRAT 201025-Nov-15 22:44
FIRAT 201025-Nov-15 22:44 
AnswerRe: Dear Sir, myOPC.dll Open Source Pin
Kurt Swaim21-Jun-20 13:24
Kurt Swaim21-Jun-20 13:24 
QuestionGracias por el ejemplo Pin
Member 112783453-Dec-14 3:18
Member 112783453-Dec-14 3:18 
BugDWORD Type read failed Pin
o_matveev10-Nov-14 22:06
o_matveev10-Nov-14 22:06 
GeneralRe: DWORD Type read failed Pin
o_matveev24-Dec-14 0:11
o_matveev24-Dec-14 0:11 
QuestionOPC with vb.net and ajax Pin
richard mclane17-Apr-14 12:18
richard mclane17-Apr-14 12:18 
AnswerRe: OPC with vb.net and ajax Pin
Kurt Swaim24-Apr-14 4:53
Kurt Swaim24-Apr-14 4:53 
AnswerRe: OPC with vb.net and ajax Pin
stixoffire8-May-15 5:21
stixoffire8-May-15 5:21 
QuestionTest With Matrikon OPC Pin
jhnlk10-Mar-14 6:50
jhnlk10-Mar-14 6:50 
AnswerRe: Test With Matrikon OPC Pin
Kurt Swaim18-Mar-14 3:57
Kurt Swaim18-Mar-14 3:57 
QuestionMultiple PLCs Pin
MuckersMate1-Jan-14 22:37
MuckersMate1-Jan-14 22:37 
AnswerRe: Multiple PLCs Pin
Kurt Swaim2-Jan-14 6:15
Kurt Swaim2-Jan-14 6:15 
GeneralRe: Multiple PLCs Pin
MuckersMate2-Jan-14 22:04
MuckersMate2-Jan-14 22:04 
Thanks for replying Kurt.

I thought that that would be the solution and that's what I've implemented although I'm worried about possible resource issues. I'm writing an alarm monitoring system which is spec'd to monitor unlimited OPC servers, each with unlimited PLCs each having unlimited devices and alarms. I'm having to instantiate a myOPC server for each group under every device. Time permitting I may attempt to modify myOPC so that one instance can manage an OPC Server entirely - I'll keep you posted.

Just one other thing which I'm investigating - the line within StartOPC when server error occurs

_ConnectedGroup.OPCItems.SetActive(1, _ActiveItemServerHandles, _ActiveState, _ActiveItemErrors)

This always excepts when an item could not be added with a cross boundary memory corruption error - any ideas?


Also, one minor thing, I would recommend that the NumItems Setter property reDims the arrays with Preserve - I'm adding to OPCItems via threads so I increment NumItems each time an item is added. I'm coming from C# so there may be performance hit I'm not aware of....
Steve

QuestionWhere is the event handler Registered & Fired Pin
subbu_s326-Nov-13 2:05
subbu_s326-Nov-13 2:05 
AnswerRe: Where is the event handler Registered & Fired Pin
Kurt Swaim26-Nov-13 4:24
Kurt Swaim26-Nov-13 4:24 
GeneralRe: Where is the event handler Registered & Fired Pin
subbu_s326-Nov-13 6:44
subbu_s326-Nov-13 6:44 
GeneralRe: Where is the event handler Registered & Fired Pin
Kurt Swaim27-Nov-13 4:33
Kurt Swaim27-Nov-13 4:33 
SuggestionOPC DA Samples Pin
thoahn18-Nov-13 0:34
thoahn18-Nov-13 0:34 
GeneralRe: OPC DA Samples Pin
ZbynekZ23-Mar-14 23:23
ZbynekZ23-Mar-14 23:23 
QuestionCan't register dll on a 64 bit machine Pin
dretjhu14-Oct-13 7:18
dretjhu14-Oct-13 7:18 
AnswerRe: Can't register dll on a 64 bit machine Pin
Jesux Manuel25-Oct-13 8:16
Jesux Manuel25-Oct-13 8:16 
AnswerRe: Can't register dll on a 64 bit machine Pin
Kurt Swaim28-Oct-13 14:49
Kurt Swaim28-Oct-13 14:49 

General General    News News    Suggestion Suggestion    Question Question    Bug Bug    Answer Answer    Joke Joke    Praise Praise    Rant Rant    Admin Admin   

Use Ctrl+Left/Right to switch messages, Ctrl+Up/Down to switch threads, Ctrl+Shift+Left/Right to switch pages.